(I) Receptacle Outlets.
Except as covered in
220.41 and
220.14(J), receptacle outlets shall be calculated at not less than 180 volt-amperes for each single or for each multiple receptacle on one yoke. A single piece of equipment consisting of a multiple receptacle comprised of four or more receptacles shall be calculated at not less than 90 volt-amperes per receptacle. This provision shall not be applicable to the receptacle outlets specified in
210.11(C)(1) and (C)(2).
(J) Receptacle Outlets in Office Buildings.
In office buildings, the receptacle loads shall be calculated to be the larger of the following:
- (1)
The calculated load from 220.14(I)
- (2)
11 volt-amperes/m2 (1 volt-ampere/ft2)