141130-1632 EST
Ohms law:
I think the 60 V reading is what everyone is concerned about, and it is always the same value.
My suggestion:
1. Disconnect all hot wires in a bundle, cable, or conduit. In other words in close proximity to each other.
2. Leave the EGC, and neutral (if there is one) connected.
3. Using high impedance meter measure voltage between EGC and neutral. This should be virtually zero. If wires are in conduit the reading might be a few millivolts. If not, then why? Voltage might be somewhat higher without the shielding of the conduit. If EGC and netural are not bonded at the panel, then expect a few volts.
4. If there is a neutral that travels with the hot wires, then use it as a reference. Otherwise use the EGC as the reference.
5. Relative to your reference measure the voltage (high impedance) of each hot wire. Should be near zero.
6. If the above are OK, then energize one hot line, and proceed with all of the above measurements. You should see the capacitively coupled voltage in high impedance, and near zero volts in the low impedance mode.
&. Describe your meter for both high impedance and low imp[edance.
.