1900 box in class 1 div 2?

Status
Not open for further replies.

jmargolis79

Member
Location
minneapolis
Can you use a 1900 box(4 square) in class 1 div2 group d? This is just for wire pulling and splicing, no arcing device. I know it would need grounding bushings or something similar. I can't find anything in the 2011 code stating that I can't. In practice I have always used nema 12 boxes but was asked today what you have to use.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
You have identified the primary issue, which NEMA 12 boxes share - properly bonding non-threaded enclosures.

You should also check Section 500.8(E)(3) for an issue not typically shared with NEMA 12 enclosures.
 