Does anyone know about a rule from 1940 about how many outlets are needed to be installed in a residential dwelling?
I usually use the issue previous to the year in question. It is difficult to know what edition was in effect in a particular year.
1937 NEC 2110: In every kitchen, dining room, breakfast room, living room, parlor, library, den, sun room, recreation room, and bed room, a sufficient number of receptacle outlets shall be installed to provide that no point on the wall, as measured horizontally along the wall, will be more than ten feet distant from such an outlet. At least one receptacle outlet shall be installed adjacent to each permanently installed laundry tub or set of such tubs.
1940 NEC 2110: Receptacle outlets shall be installed in every kitchen, dining room, breakfast room, living room, parlor, library, den, sun room, recreation room, and bedroom. One receptacle outlet shall be provided for every 20 linear feet or major portion thereof of the total (gross) distance around the room as measured horizontally along the wall at the floor line. The receptacle outlets shall, insofar as is practicable, be spaced equal distances apart. At least one receptacle outlet shall be installed for the connection of laundry appliances.
Also in 1940 came the requirement for #12 to 'food rooms' and such:
1940 NEC 2109: In dwelling occupancies, branch circuits which supply receptacle outlets in kitchen, laundry, pantry, dining room, and breakfast room, shall not supply other outlets, and such circuits shall not have conductors smaller than No. 12.
But as others have rightly pointed out, that (cloth-covered) wiring is generally nearing the end of its useful life . . .