under slab conduit in dentist office

Status
Not open for further replies.

tyha

Senior Member
Location
central nc
does the conduit in a dentist office going btween the wall and the center console for equipment need to be rigid if its under slab
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with rcarroll.

The conduits run in the slab that supply equipment in the patient care area of a dentist office must comply with 517.13.

Chris
 

220/221

Senior Member
Location
AZ
does the conduit in a dentist office going btween the wall and the center console for equipment need to be rigid if its under slab

Yes. I couldn't believe my eyes when I first read this several years ago. Absolutely stupid in my opinion. You want a 100% failsafe ground? Conduit aint it.
 

220/221

Senior Member
Location
AZ
For all practical pupose, especialy in this discussion, IMC = RMC.


EMT under slab isn't allowed in all areas (like here). I was quite surprised to learn that NEC allows it.

RMC/IMC doesn't last long underground here either, even when it's pipe wrapped.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO the inside of the PVC would be a wet location which would prohibit the use of AC cable.
 

Chris6245

Senior Member
Location
Ohio
IMO the inside of the PVC would be a wet location which would prohibit the use of AC cable.

If the PVC went "under" the slab I would agree....But if the PVC is "in" the slab and the slab is inside the building, How could it be considered a wet location?
 
Patient care

Patient care

If it is a patient care area you can use any metallic raceway listed for the application. MC , Rigid metallic, EMT , Imc , .
GOOD LUCK !!
Keep reading it until you understand. Eventually you will see the light.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the PVC went "under" the slab I would agree....But if the PVC is "in" the slab and the slab is inside the building, How could it be considered a wet location?


Even a conduit within the concrete would be a wet location if that concrete was in direct contact with the earth. I agree that a conduit in a slab on a floor that is not in contact with the earth wouldn't be a wet location.

Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Even a conduit within the concrete would be a wet location if that concrete was in direct contact with the earth. I agree that a conduit in a slab on a floor that is not in contact with the earth wouldn't be a wet location.

I agree with this and if I had my book I would give you the code article.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with this and if I had my book I would give you the code article.

Here is the definition of wet location:

Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.

Chris
 

dcspector

Senior Member
Location
Burke, Virginia
I had one where the EC ran RMC in slab and stubbed up below chair. The EC pulled HCF MC should a bond bushing be installed on the RMC stub up below the chair? Yes the MC was pvc coated.
 
Last edited:

rcarroll

Senior Member
I had one where the EC ran RMC in slab and stubbed up below chair. The EC pulled HCF MC should a bond bushing be installed on the RMC stub up below the chair? Yes the MC was pvc coated.

Pretty expensive run, IMO
I say if the MC is rated for wet location & the sheathing is a ground path, which apparenly it is, no bond bushing required.
 

Chris6245

Senior Member
Location
Ohio
Here is the definition of wet location:



Chris

OK....But what is between the concrete and "earth" 90% of the time? (at least in my area of the country) Pea Gravel and Visqueen...So is the concrete in "DIRECT CONTACT" with the earth? IMO no. Around here (Ohio) I very rarely see concrete poured directly on dirt.
 

iwire

Moderator
Staff member
Location
Massachusetts
OK....But what is between the concrete and "earth" 90% of the time? (at least in my area of the country) Pea Gravel and Visqueen...So is the concrete in "DIRECT CONTACT" with the earth? IMO no. Around here (Ohio) I very rarely see concrete poured directly on dirt.

I agree that if there is plastic under the slab then the slab is not in direct contact with the earth ............ That said, it is not a hair I would leave to split with the inspector, I would treat it as a wet location and use suitable conductors in it.
 