I was doing a estimate for old house sale or home inspection punch list.
this located in aone of the few parts of town with residential 3ph power.
100amp 3p service without a main breaker.
orginally built in 1940s ? with added and a addonon added on and a 1970's mother-in-law addition. grandpa did somework here and there. overall well maintained and in good shape appox 2800 sq ft
I opened upthe sq d panel to find why it was 3ph but had 4 single breaker in a line???
Iexpected to find a wild leg setup-
I had to triplecheck and go get my other meter I found that the top 3ph breakers had wild leg -----but ----------the lower breakers were only 2-pole?????
has any body ran into a similar panel???
I seen similar housed built in that time frame for early 3ph A/C systems, but never a special panel as such.
I did not ahve time to pull breakers to check the bus bars, but the lower visable buses below the breaker only had phace A-C visable and a space for "B" ????
NOw for the BIG DELIMIA
The mother-in-law addition appears to be fed by a 3PH 60 BREAKER ----but--
upon inpection of the sub-panel it appears to be 3phase panel w/main HOWEVER-- it is fed 60amp phase A-C-A instead of A-B-C !!!!
I can tell that this is where the sub-panel installer may figured out his mistake(OR NOT) and installed all the 2pole breakers in a skipped order to acheve 240 instead of 120/120 same phase
WHAT DO YOU TELL THE CUSTOMER??????
I talked quietly to the home inspection who happened to be there on afollow-up. The report was very through accurated and well done, and caught the standard/typical problems. but knowing the difference between a 3ph wild leg system or a single 30amp one leg systemwas above is training level.
other than that, I know the realtor/buyer/seller does not want me to cry chicken little and blow the sale. what should i do ,, I would have to get the chalkboard out to explain it the the buliding inspector. I really donot want get him involved unless asked to
Most items on the puch list are easy to fix, open splice/mssing gfi etc
I could fixthe items on the list, make few $$ and run---OR--- or cry wolf and loseout???
times are tuff and work is slower. DENNIS
this located in aone of the few parts of town with residential 3ph power.
100amp 3p service without a main breaker.
orginally built in 1940s ? with added and a addonon added on and a 1970's mother-in-law addition. grandpa did somework here and there. overall well maintained and in good shape appox 2800 sq ft
I opened upthe sq d panel to find why it was 3ph but had 4 single breaker in a line???
Iexpected to find a wild leg setup-
I had to triplecheck and go get my other meter I found that the top 3ph breakers had wild leg -----but ----------the lower breakers were only 2-pole?????
has any body ran into a similar panel???
I seen similar housed built in that time frame for early 3ph A/C systems, but never a special panel as such.
I did not ahve time to pull breakers to check the bus bars, but the lower visable buses below the breaker only had phace A-C visable and a space for "B" ????
NOw for the BIG DELIMIA
The mother-in-law addition appears to be fed by a 3PH 60 BREAKER ----but--
upon inpection of the sub-panel it appears to be 3phase panel w/main HOWEVER-- it is fed 60amp phase A-C-A instead of A-B-C !!!!
I can tell that this is where the sub-panel installer may figured out his mistake(OR NOT) and installed all the 2pole breakers in a skipped order to acheve 240 instead of 120/120 same phase
WHAT DO YOU TELL THE CUSTOMER??????
I talked quietly to the home inspection who happened to be there on afollow-up. The report was very through accurated and well done, and caught the standard/typical problems. but knowing the difference between a 3ph wild leg system or a single 30amp one leg systemwas above is training level.
other than that, I know the realtor/buyer/seller does not want me to cry chicken little and blow the sale. what should i do ,, I would have to get the chalkboard out to explain it the the buliding inspector. I really donot want get him involved unless asked to
Most items on the puch list are easy to fix, open splice/mssing gfi etc
I could fixthe items on the list, make few $$ and run---OR--- or cry wolf and loseout???
times are tuff and work is slower. DENNIS