1950 Sub panel / No Ground
davedottcom
I need to ground a #8 in an existing (1950's) 200 Amp 208V. 3-phase sub panel that has No grounds in either the feeder conduit or ANY of the branch circuit conduits. (All EMT) The 2" EMT feeder only has 4 Conductors 3 phases and a neutral. The Neutral is terminated on a "Neutral Buss" that is NOT bonded to the panel.
I think installing a ground bar kit on the metal frame of the panel is the correct way to go....NO bond between it and the neutral. Another Electrician told me it would be acceptable to terminate the branch circuit ground onto the neutral bar because it is a "Pre-existing" situation, but I think he's wrong. Am I right in thinking he's wrong!?!?!?
Dave
[ June 05, 2003, 09:56 PM: Message edited by: davedottcom ]
Re: 1950 Sub panel / No Ground
Perfectly good job. The EMT is the ground conductor. Install a ground bus and connect the #8.
Bennie, I accidently sent the post before I was finished writing it! I edited it and finished the question now. That is exactly what I thought. Thanks.
Dave
This installation appears to meet present code.
The electricians in the 50s were pretty good ;)