Hi Roger, (house is a 1963 not a 1953.. ..I would like to install the ARK - fault, as installing receptacles will trip even from walking and creating static with the carpet
Never seen AFCI or GFCI breakers for Federal Pacific Electric equipment.
Unless using type BR sub-panels, you are stuck with AF/GF outlet replacements in locations specified by NEC 210.12
Static-charge buildup is felt from fingers touching cover-plate screws, but proper 3-conductor cables with grounding discharge static along Equipment Grounding Conductors, or the Grounding Electrode System. Reset devices tied to Hot & Neutral should not see static discharged along grounding paths.
Perhaps your 1960's 2-wire outlets are "bootleg" wired. An illegal pig-tail from Neutral to device Grounding yolks would re-direct static discharge from cover-plate screws to Neutral, monitored by AFCI or GFCI electronics.
4-35k volts (en.m.wikipedia.org/wiki/Static_electricity) may even destroy electronic reset devices monitoring micro amps at much lower voltages.