My library is quite limited,but here's what I found:
1956 NEC, 2351 a. ". . .disconnecting means. . . located at a readily accessible point nearest to the entrance of the conductors, either inside or outside building wall."
1965, similar language at 230-70 (b)
1975, is at 230-72 (c)
1984, is at 230-70 (a)
All my other books are newer, so I don't know about 1897-1956, but suspect that it's been there all along
I asked for proof and you found it so I'll admit that I was wrong. It's one of those things I had to see to believe.