C canman Member Apr 28, 2004 #1 Does anyone know if a 10-2 w/bare ground was legal on a dryer outlet in 1984? Thanks.
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Apr 28, 2004 #2 Re: 1984 dryer outlet It has never been legal as far as I know.
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 28, 2004 #3 Re: 1984 dryer outlet I second Johns post, it wasn't legal in 84. It required three insulated conductors, 10/3 with out ground was a common item. Roger
Re: 1984 dryer outlet I second Johns post, it wasn't legal in 84. It required three insulated conductors, 10/3 with out ground was a common item. Roger
rcarroll Senior Member Location Fort Collins, Colorado Apr 28, 2004 #4 Re: 1984 dryer outlet A bare ground was ok if it was part of an SE cable & originated from a main breaker panel & not installed in a mobile home.
Re: 1984 dryer outlet A bare ground was ok if it was part of an SE cable & originated from a main breaker panel & not installed in a mobile home.