1P, 120V branch wire color in 120/208Y panel

ETEL64

Member
Location
Magnolia, TEXAS, USA
Occupation
Project Manager - The Reynolds Company
I have a 3PH, 4W 120/208Y panel with a full complement of 1P breakers across all 3 phases.

Does each 1P branch breaker wire color need to indicate by color the phase it is on?

Black wire - Ckt 1 --- Ckt 2 - Black wire
Red wire - Ckt 3 --- Ckt 4 - Red wire
Blue wire - Ckt 5 --- Ckt 6 - Blue wire
 
Last edited:
If the premises has more than one voltage system you are required to identify the circuits in a distinct manner. Most often this is bu color.
See 210.5 & 200.6
If there are not two voltage systems then the only requirement is to identify grounded and grounding distinctively, not the phase conductors.
 
If the premises has more than one voltage system you are required to identify the circuits in a distinct manner. Most often this is bu color.
See 210.5 & 200.6
If there are not two voltage systems then the only requirement is to identify grounded and grounding distinctively, not the phase conductors.
Unless it's a Delta Highleg.
The B phase is orange.
🐴 beating a dead horse here.
 
Unless it's a Delta Highleg.
The B phase is orange.
Seems to depend on where/when the system was installed. When I was doing VFD field work out of Cleveland, orange was B phase regardless of the configuration. When I went to Columbus, orange became delta high, while B phase on wye was violet.
 