Ohm eye cod.
I can't believe anyone would exceed the bending radius of THHN like that.
What bending radius?
Ohm eye cod.
I can't believe anyone would exceed the bending radius of THHN like that.
It's a BFBHDD. (Back-fed breaker hold-down device.)What are the red plastic things on the buss side of that backfed main breaker?
Same thing here. And the HO told me that the city should have a pamphlet, telling you how to do this..I Said "we do, it's about 822 pages.I don't want to get into an HO doing his own work debate, because to me as long as it's done right I don't care. Now the story
Had this same install on a service change, using the old panel as a sub, and told the homeowner that he needed to change it. So he did, except that he didn't move the grounded and grounding conductors coming from the main and he fried some electronics in the house. "But that's what you said to do" "No it wasn't, and you should have asked if you didn't understand."
Same thing here. And the HO told me that the city should have a pamphlet, telling you how to do this..I Said "we do, it's about 822 pages.![]()
That section deals with the bending of conductors over 600V.300.34
That section deals with the bending of conductors over 600V.
Even 312.6 is about the amount of space required to be available for bending conductors and inserting them into the terminations. There is nothing in the NEC that provides a minimum bending radius of the actual 600V conductor inside of an enclosure. I am not aware of individual conductors like THHN having any minimum bending radius at all.