2/0 in emt

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: 2/0 in emt

This type of question generally depends on the type of conductor. For THHN, as an example, you need 2 inch. For RHH, a 2 inch will hold 4 conductors of size 2/0, but in order to figure out whether a ground would also fit you need to calculate the actual areas of the conductors. But you can find this information in Annex C of the NEC.
 
Re: 2/0 in emt

thanks, i don't have a copy of the NEC...a customer of mine was asking me, so i will pass along the info. I will sell him 2&1/2 just to be safe, thanks for the help
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Re: 2/0 in emt

Can someone shed some light on how to determine whether you use Table 8, conductor properties, or Annex C, conductor insulation for fill calculations.