2-1/2″ Meter Offset - Where can I find one?
Dave Sampson
MO
EE
Hi all,
Can someone show me where to find a 2-1/2″ PVC Meter Offset in the US?
I can find 1-1/2" and 2" everywhere locally... 2-1/2" in Canada on-line. But nowhere in the US!
I've for 6 - 3/0 running through it, so 2" won't work as the max is 5 - 3/0 in a 2"
Thanks all!
This is a 320a meter feeding into two vertically stacked 200a disconnects.
6 - 3/0 wires coming out of the meter through the 2 1/2" meter offset into the bottom disconnect. 3 of the 3/0 connect to that disconnect, the other 3 go through the hub at the top of that box into the bottom of the second disconnect
That is correct for 40% fill on 2" Schedule 40 for 3/0 THWN-2 conductors. However, based on your description, the total run between enclosures sounds like it's under 24", in which case you may use 60% fill per Chapter 9 Table 1 Note 4. Meaning a 2" conduit would be OK for (6) 3/0 THWN-2.
Cheers, Wayne
IPEX makes them. Maybe get one online.