tryinghard
Senior Member
- Location
- California
Scenario:
1 3ph 2hp 240v motor = 6.8, includes starter
1 3ph 1hp 240v motor = 4.2, includes starter
Would like to have these on one circuit, wouldn?t this arrangement be considered a feeder rather than a branch due to the OL?s?
If so 430.62(A) applies rather than 430.53 and OCP sizing would be:
17 = 6.8 x 2.50 for the 2hp
4.2 = 1hp (4.2 x 2.5 = 10.5)
21.2 = OCP
Therefore the maximum acceptable, inverse time, breaker size would be 15A in light of 430.62(A), 20A is too large.
Is this correct, any other thoughts?
1 3ph 2hp 240v motor = 6.8, includes starter
1 3ph 1hp 240v motor = 4.2, includes starter
Would like to have these on one circuit, wouldn?t this arrangement be considered a feeder rather than a branch due to the OL?s?
If so 430.62(A) applies rather than 430.53 and OCP sizing would be:
17 = 6.8 x 2.50 for the 2hp
4.2 = 1hp (4.2 x 2.5 = 10.5)
21.2 = OCP
Therefore the maximum acceptable, inverse time, breaker size would be 15A in light of 430.62(A), 20A is too large.
Is this correct, any other thoughts?