I have often wondered if the exception to 445.13 could be used when the actual current the generator can produce is lower then the rating of the breaker on it, many gen sets have electronic current limiting to prevent from burning up the generator, some are just by design not able to produce more current because the motor will start to stall out, but we all know in the case of a fault wither line to line or line to ground that smaller conductors will take the fault since the OCPD will open fast, what if the generator has built in over current protection, can we adjust to this using the exception when the only thing the 100 amp breaker does is protect for faults? a 20kw generator will only produce 83 amps so why do we have to size the conductors + 25% to the 100 amp breaker and not to the actual current the generator is capable of? also many gen-sets will have a reduced rating when run on NG verses propane, so can we use this lower rating when sizing our conductors? do we really need to size off the breaker on the generator when the rating of it can be much lower?
Just kind of throwing this out, so don't take it as a can do.