Working on a lot of commercial offices lately it would seem, with many of them having very large Open Office concepts. I keep running into Furniture systems that utilize the (2+2) electrical system, essentially meaning that 2 sets of 2 circuits, where the 2 circuits in each set share a neutral and a ground. My question is, we typically power 4-6 workstation pods with (2) 120V circuits, and have the contractor use a circuit on each of the 2 sets, simple as that. The current contractor is pushing back and saying he's only ever done it to where both circuits HAVE to share the same neutral and ground so they have to both be on the same set, but then wouldn't that mean I'd need a 2P breaker back at the source such that they have the same disconnecting means? And even if so, is there anything wrong with the approach we've been doing? I can't find where it wouldn't be code-compliant to just use one circuit off each set and be done with it

Thanks in advance!
 
So there are 2 sets (2+2) each set has 2 hots/neutral?

Your method: set 1 use one hot and and the neutral. Set 2 use one hot and the neutral.
Yes, each set has 2 hots, and a neutral and a ground (neutral and ground intended to be shared)

My method, use one hot, one neutral, and one ground off each set, such that they both have their own neutral and ground.
If 6 workstations, you'd essentially have 3 on each circuit.

Contractor is saying he wants to use exclusively one set and share the neutral and ground.
 
Your method's better, and as infinity says, code compliant, but also check the mfr instructions. While remodeling one of our offices, the structured wiring inside the cubicles we chose had this weird three hot, two neutral, one ground thing going on where one set of hots plus neutral went to the desk-level receptacles (where you'd plug in things like a desk lamp, coffee heater, transitory gear being configured), and a second set of hot+neutral went to the floor for the more permanently installed gear (workstations, monitors, printer if you had one).
 
Your method's better, and as infinity says, code compliant, but also check the mfr instructions. While remodeling one of our offices, the structured wiring inside the cubicles we chose had this weird three hot, two neutral, one ground thing going on where one set of hots plus neutral went to the desk-level receptacles (where you'd plug in things like a desk lamp, coffee heater, transitory gear being configured), and a second set of hot+neutral went to the floor for the more permanently installed gear (workstations, monitors, printer if you had one).
Thanks, the one page cutsheet says the below, so I'm assuming the intent is also to have computers and such equipment that could be deemed sensitive on one (isolated) circuit and other less sensitive equipment on others.

2+2 Electrical System
The Dividends Horizon 2+2 electrical system
is designed for areas where power usage is
significant and sensitive electronic equipment
requiring two isolated circuits are required.
The wiring configuration of the (2+2)
electrical system is (see chart):
• Hot ‘‘A’’ (black)
• Hot ‘‘B’’ (red)
• Shared neutral ‘‘N1’’ (white/black) for circuits #1 and 2
• Shared ground ‘‘G1’’ (green, bare copper) for circuits #1 and 2
• Hot ‘‘Y’’ (tan)
• Hot ‘‘X’’ (pink)
• Isolated Shared Neutral ‘‘N2’’ (white/red) for circuits #4 and 5
• Isolated Shared ground ‘‘G2’’ (green/yellow) for circuits #4 and 5
Circuits 1 and 2 share common neutral and ground. Circuits 4 and 5 share a separate common neutral and ground.
 
Circuits 1 and 2 share common neutral and ground. Circuits 4 and 5 share a separate common neutral and ground.
The neutrals are both the same, one for A&B the other for X&Y. The EGC for A&B is used for all equipment grounding and bonding, the EGC for X&Y is isolated within the furniture system.
 
I’ve run into the same thing—most of those modular systems with pre-wired whips are UL-listed under 2.2 and as long as it's all labeled and installed per instructions, inspectors are usually good.
 
Ran into the same kind of setup on a few office projects—splitting circuits across sets can work fine as long as the loads are balanced and breakers match code. Took a bit to convince the contractor, but once we showed the layout and load calculations, it clicked. For extra ideas on arranging workstations and even small office setups, here on the Outdoor Living Blog for garden furniture in the UK had surprisingly useful tips that got me thinking differently about spacing.
 