So is a 400 a service the same as say 2- 200a panels? I'm proposing a service for a job 400a meter with double lugs on the load side and I'm thinking to run two sets of 3/0 , one set each to s 200a panel from those double lugs , the line would be one set of 500s
500s are rated for 395 so the next size up is 400. Am I on with the 3/0 or do I run a set of 500s to a wireway/trough and tap to 3/0 to feed my panels?
On another note is it acceptable to feed two 200a panels off of one set of 3/0 with a 200a meter . I say no GC
Sent from my SM-G965U using Tapatalk
500s are rated for 395 so the next size up is 400. Am I on with the 3/0 or do I run a set of 500s to a wireway/trough and tap to 3/0 to feed my panels?
On another note is it acceptable to feed two 200a panels off of one set of 3/0 with a 200a meter . I say no GC