2 4ton cac units 125' from panel.
I'd pull # 2/3 SER AL., just to cover my ass and charge accordingly because the specs were not present. Plus this gives options later on when they need to add something. Win/Win in my book. I bet i come out cheaper than the copper you propose to run.
Sure, why not? Set a little sub panel and maybe not even need any disconnect other than the breakers. There is probaby a service receptacle needed if there isn't already one there.
And one day the may need to power a pole light or fountain or who knows what. I'm starting to like SER AL since the price of copper has gone up these last few years. :D:D It doesn't weigh much either and that's a consideration for a lazy person.
Exactly, I do this setup all the time... plus I can staple it to the bottom of the joists, no drilling required.
Reason I brought this up is because of a TC. Same units, older house shorter run, but #6 was used and the units were tripping the 60 amp breaker. Now I am fixing to wire similar but longer run.
If these units where triping the breaker I would look at something other than the size of the wiring to be the issue. The #6 and #8 copper that I posted al came slightly less than 2% loss.
Over- charge, long line application not used, equipment not matching, etc.