Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
I'm running #2 AL SER inside the house, then changing to underground conduit with single #2 AL conductors to a subpanel for a detached garage. #2 AL will carry 100 amps right? I had one inspector a few years ago that said no. He said the single conductors would but the cable would not. 310.15 services for dwellings says 100 amps. But he and his county did not allow the #2 SER cable to be used for 100 amps. He finally said the reason was: a detached garage is NOT a dwelling and therefore table 310.15 does not apply for the cable. Any thoughts ?? Thank you