Hey Guys-
I sat in today on a meeting between (2) different localities and the following came up and man you would have died to be a fly on the wall. Lets see how you all feel.
1.) The service latteral is coming into a 3 gang meter base. There is a main breaker panel in each tenent space.
One locality said they consider this one building and one service and that they must install exterior service disconnects under each meter socket for each space.
One locality said they are all seperate tenent spaces and out of the meter enclosure each are considered service conductors to the panels in each unit and do not need to be grouped.
There was indeed fire walls or fire rated ceilings between all given spaces....now from the drawing I saw one of them will have a service disconnect outside anyway because they could not meet the 230.70...so they said since that unit had to have a service disconnect at the meter...they all had to....lol
Here was how it was wired not to the best I can gather....3 gang meter base, the center meter is back to back with the retail space main breaker panel and the meter on the right feeds a service disconnect on the outside of the wall and then on to the panel in the one dwelling space.....the other meter socket on the left has no exterior disconnect and feeds a panel on the second floor up the side of the building...
They spent nearly 3 hours ranting back and forth over it.....any thoughts
I sat in today on a meeting between (2) different localities and the following came up and man you would have died to be a fly on the wall. Lets see how you all feel.
1.) The service latteral is coming into a 3 gang meter base. There is a main breaker panel in each tenent space.
One locality said they consider this one building and one service and that they must install exterior service disconnects under each meter socket for each space.
One locality said they are all seperate tenent spaces and out of the meter enclosure each are considered service conductors to the panels in each unit and do not need to be grouped.
There was indeed fire walls or fire rated ceilings between all given spaces....now from the drawing I saw one of them will have a service disconnect outside anyway because they could not meet the 230.70...so they said since that unit had to have a service disconnect at the meter...they all had to....lol
Here was how it was wired not to the best I can gather....3 gang meter base, the center meter is back to back with the retail space main breaker panel and the meter on the right feeds a service disconnect on the outside of the wall and then on to the panel in the one dwelling space.....the other meter socket on the left has no exterior disconnect and feeds a panel on the second floor up the side of the building...
They spent nearly 3 hours ranting back and forth over it.....any thoughts