Customer wants to connect a single generator to two different buildings (house and detached garage). Both buildings are fed from a common utility transformer but each building is metered seperately (and have individual service entrance disconnects after the meters).
Right now each building has the grounded conductor (neutral) bonded to the ground bus (grounding electrode)at the service entrance disconnect.
The intent is to conect the generator output to both buildings (via seperate transfer switches)
The generator is not a seperatly derived source. (the frame is connected to grounding electrode but there is not a bonding jumper between the neutral and ground)
The neutral in the transfer switches are "unswitched" therefore, if I connect the generator neutral to both buildings (via a bus bar in a j-box), the neutrals for both buildings are then connected.
Should I disconnect the main bonding jumper (between the grounded conductor and the grounding electrode) in ONE of the service entrance disconnects? (i.e. - isolated the neutral in one panel)
The plan would be to tie all the equipment grounding conductors (both service entrance panels and generator frame) together.
Right now each building has the grounded conductor (neutral) bonded to the ground bus (grounding electrode)at the service entrance disconnect.
The intent is to conect the generator output to both buildings (via seperate transfer switches)
The generator is not a seperatly derived source. (the frame is connected to grounding electrode but there is not a bonding jumper between the neutral and ground)
The neutral in the transfer switches are "unswitched" therefore, if I connect the generator neutral to both buildings (via a bus bar in a j-box), the neutrals for both buildings are then connected.
Should I disconnect the main bonding jumper (between the grounded conductor and the grounding electrode) in ONE of the service entrance disconnects? (i.e. - isolated the neutral in one panel)
The plan would be to tie all the equipment grounding conductors (both service entrance panels and generator frame) together.