If the conduit is larger than 2" it needs a seal. 501.15(A)(1)(2)
This aspect is a little confusing - if you look closely at 501.15(A)(1)(2) it states enclosure
"entry is metric designator 53 (trade size 2) or larger..."
to me this indicates a 2" conduit run could be reduced to a 1-1/2" hub at the enclosure entry and would not need a seal.
However, if you look at Commentary Table 501.1 it states seal is required "If conduit is size 2 or larger, in conduit run within 18" of enclosure"... it doesn't say anything about the enclosure entry size.