Jim W in Tampa
Senior Member
- Location
- Tampa Florida
If in a home i add a new dryer outlet it needs to be 4 wire.That part is easy.Question is what if the new dryer sits right next to and old dryer that is 3 wire .Will there be a hazard ?
They both are being fed from a subpanel.If they touch i am thinking i might cause a hazard.roger said:It would be no more dangerous than it was before the new dryer was installed, unless of course there was no grounded surfaces with in touching distance before.
Roger
Jim W in Tampa said:They both are being fed from a subpanel.If they touch i am thinking i might cause a hazard.
If fed from a _subpanel_, then the old circuit _must_ be changed to a 4 wire circuit.
I believe, but cannot confirm, that using a three wire circuit for dryers has _never_ been permitted from a subpanel, and that this use is not grandfathered.
Jim W in Tampa said:They both are being fed from a subpanel.If they touch i am thinking i might cause a hazard.
curt swartz said:If the existing receptacle is fed with 2-wire SE cable I agree with the other here. If it is fed with 10-3 NM with or without EGC I say the existing installation is code compliant. The commentary in the 93 Handbook also states that the circuit only needs to originate from the service panel if type SE cable with a bare neutral is used. I realize the commentary is not code but……..
From the 93 NEC:
250-60(c) The grounded conductor is insulated; or the grounded conductor is uninsulated and part of a type SE cable and the branch circuit originates at the service equipment.
How would an inspector handle this ? The old is legal and so is the new.
Jim W in Tampa said:Its my own house and i do want it safe.Hardest part will be buying another cord and receptacle (ouch).
It?s not that simple, Chris. Article 80.9(B) is the NEC article that permits an existing installation that does not comply with the current code to remain in operation. It?s in the Annex now, so it is not even a mandatory article. But it does require that the AHJ be satisfied that the non-conforming condition not present an imminent danger to occupants.raider1 said:If the existing installation is code compliant and the new is code compliant then there is no problem.
charlie b said:
Now consider a 3-wire dryer and 4-wire dryer side by side. Put one hand on each dryer. It does not even matter if the 4-wire dryer is running. There can be a path for neutral current to flow, as follows: From the neutral point (of the 3-wire dryer) to the frame, to your right hand, through your chest to your left hand, to the frame of the 4-wire dryer, via the EGC to the N-G bond point, and now you are back at the source. Now please note that planet Earth is no longer part of the path. Instead, a low-resistance conductor (the EGC) takes the place of dirt in this scenario. The current will be higher; of that I am certain. But whether it will be enough to be a real danger, I cannot say without taking time (that I don?t have just now) to do some math. Perhaps someone else can chime in here.
Charlie...good point.
What is the difference between your installation and one having a grounded washing machine sitting beside a 3-wire dryer?
That's pretty common (my home included).
If the 3-wire dryer loses it's neutral and you touch it and the washing machine at the same time you're going to get shocked.
Requiring 4-wire dryer circuits will eventually eliminate this possible threat, but what about the thousands of existing circuits?
just a thought
steve
charlie b said:It?s not that simple, Chris. Article 80.9(B) is the NEC article that permits an existing installation that does not comply with the current code to remain in operation.
hillbilly said:What is the difference between your installation and one having a grounded washing machine sitting beside a 3-wire dryer?
That's pretty common (my home included).
If the 3-wire dryer loses it's neutral and you touch it and the washing machine at the same time you're going to get shocked.
Requiring 4-wire dryer circuits will eventually eliminate this possible threat, but what about the thousands of existing circuits?
gary said:A simple and inexpensive way to address your concern would be to simply bond the two dryers together with a piece of #10 THHN. :wink:
hillbilly said:charlie b said:
Now consider a 3-wire dryer and 4-wire dryer side by side. Put one hand on each dryer. It does not even matter if the 4-wire dryer is running. There can be a path for neutral current to flow, as follows: From the neutral point (of the 3-wire dryer) to the frame, to your right hand, through your chest to your left hand, to the frame of the 4-wire dryer, via the EGC to the N-G bond point, and now you are back at the source. Now please note that planet Earth is no longer part of the path. Instead, a low-resistance conductor (the EGC) takes the place of dirt in this scenario. The current will be higher; of that I am certain. But whether it will be enough to be a real danger, I cannot say without taking time (that I don?t have just now) to do some math. Perhaps someone else can chime in here.
Charlie...good point.
What is the difference between your installation and one having a grounded washing machine sitting beside a 3-wire dryer?
That's pretty common (my home included).
If the 3-wire dryer loses it's neutral and you touch it and the washing machine at the same time you're going to get shocked.
Requiring 4-wire dryer circuits will eventually eliminate this possible threat, but what about the thousands of existing circuits?
just a thought
steve
I never gave that a thought.Its been that way for many years.Guess we were lucky.When i went to big orange for the cord my thinking was why not make it legal for the extra few bucks.But rest assured the old will be brought up to code.