Patmandad
Member
- Location
- Vallejo, Ca, Solano
i have a situation in an intermediate data closet where I have 1 breaker space in my emergency power panel and I need 2 circuits. can I run #10 on a a 30 amp breaker to 2 single 5-20R?
Correct.IMO, Table 210.21(B)(3) says no. You can use #10 but only a 20A breaker.