roy g
roy g
table 4 of chap 9 lists 2"emt at 40% fill of 1.342 sq in..
table 5A of chap 9 (compact strand copper or alum) lists 4/0 XHHW @ .2733 sq in. x 4 = 1.093 sq in and # 4 @ .073 sq in. for total of 1.166 sq in. which allows this to be installed in 2" cond.
also same table allows thhn (total area 1.19 in) to be used. Most wiring supplied by distributors in this area is now compact strand conductors. As stated by others, this may not be answer to question on exam or pratical to install depending ion run, it will meet intent of code