2 family dwelling

Status
Not open for further replies.

nizak

Senior Member
It's been many years since I've done a duplex.

Is it still code compliant to run the feeder conductors from the disconnect through the basement of one half to get to the other?

Thanks
 

kwired

Electron manager
Location
NE Nebraska
It's been many years since I've done a duplex.

Is it still code compliant to run the feeder conductors from the disconnect through the basement of one half to get to the other?

Thanks

I see nothing in 215 that would prohibit this, can't think of anywhere else such rule would be if it exists.

Service conductors can't pass through another building/occupancy.

Might be some issues with Art 225 feeders to separate buildings but I don't think that applies to what you have.
 