N nizak Senior Member Jul 15, 2019 #1 It's been many years since I've done a duplex. Is it still code compliant to run the feeder conductors from the disconnect through the basement of one half to get to the other? Thanks
It's been many years since I've done a duplex. Is it still code compliant to run the feeder conductors from the disconnect through the basement of one half to get to the other? Thanks
kwired Electron manager Location NE Nebraska Occupation EC Jul 15, 2019 #2 nizak said: It's been many years since I've done a duplex. Is it still code compliant to run the feeder conductors from the disconnect through the basement of one half to get to the other? Thanks Click to expand... I see nothing in 215 that would prohibit this, can't think of anywhere else such rule would be if it exists. Service conductors can't pass through another building/occupancy. Might be some issues with Art 225 feeders to separate buildings but I don't think that applies to what you have.
nizak said: It's been many years since I've done a duplex. Is it still code compliant to run the feeder conductors from the disconnect through the basement of one half to get to the other? Thanks Click to expand... I see nothing in 215 that would prohibit this, can't think of anywhere else such rule would be if it exists. Service conductors can't pass through another building/occupancy. Might be some issues with Art 225 feeders to separate buildings but I don't think that applies to what you have.