From one service point (one to six disconnects) you can install as many feeder panels as you wish in one in one structure.
Where are the red/blue conductors going to connect ? and where do they terminate ?
You can use one SUSE MLO panelboard with up to 6 disconnecting means per service entrance conductor.....
I see, I thought that this is correct only if you are installing different meters in one service, something like is in the image bellow.
But, As I understood you, is correct to install a panelboard without main breaker and also use it to install different breakers to fed different loads, then the photograph shown below is correct, right?.
...
And why I don't see green wires from left and top conduits?
You can use one SUSE MLO panelboard with up to 6 disconnecting means per service entrance conductor.
230.7 1 and 408.36 Exception 1 allow a MLO (no main) panel-board with up to 6 breakers as the service disconnect provided the panel-board meets 230.66 and is capable of carrying the load.
I see no way the unconnected wires can be connected without producing violations.
230.7 1 and 408.36 Exception 1 allow a MLO (no main) panel-board with up to 6 breakers as the service disconnect provided the panel-board meets 230.66 and is capable of carrying the load.
I see no way the unconnected wires can be connected without producing violations.
As 230.66 states, the panelboard shall be marked to identify it as being suitable for use as service equipment (SUSE). So look at the panelboard label. A typical indicator is if the panelboard is furnished with a green machine screw that when installed, bonds the [otherwise isolated] neutral bar to the enclosure/EGC bus terminal. The screw serves the purpose of the main bonding jumper(MBJ). In some panelboards, it is a bonding strap (usually not greenOne more question, what kind of panel-board meets the requirements of the section 230.66?, I mean, the panel-board of the picture could work for this?