kbsparky said:I believe that those numbers are in there as a convenience, to save you time looking up in the book for the same information.
The Code requires that non-metallic boxes be ".... durably and legibly marked by the manufacturer with their volume..." [see 314.16(A)(2)] The Code does not require that the number of conductors be included with this information. The manufacturers provide that additional information as a convenience to the installer.
According to my calculations, a typical 36 cubic inch 2-gang box is capable of holding 12 #8 AWG conductors. Deducting 2 for the device and another one for built-in clamps still allows for 9. Terminating a #8/3G cable into that box under those conditions means you have more than double the space requirements available.
I know it states a deduction of 2 conductors per yoke, but wouldn't you have to deduct 4 conductors since the range receptacle takes both sets of mounting holes in the box? In other words, I know the piece of metal Yoke for the range receptacle is only one piece, it does consist of four slots for securing the device at four different points in the two gang box, therfore effectively taking the room of 2 yokes and therefore the deduction of 4 conductor sizes.
I also know that the answer is moot to this example, as there would still be ample room of conductor fill for the box. Just curious as to how you view it.
edited for spelling