Could I get some opinions please.
A municipal facility has proposed adding 2 5kw portable generators as a backup to the backup automatic generator that picks up the entire building load upon utility failure. The proposal is to install 2 - 30 amp inlets at the same location on the exterior of building. From each inlet we go to a manual transfer switch ajacent to the sub panel served (both sub panels are in the same building but in different locations). These 2 portable generators are not electrically connected in any way. The plan is for these generators to operate at the same time: #1 for the panel that powers the well pump, #2 for the panel that powers vital communications.
Also would there have to be a disconnect for each generator grouped together at the point of entry of both generator feeders? Would the twist lock at each inlet suffice as the required disconnects? The transfer switches are well inside the building.
After thinking on this for several hours a light went on in my head...
Would having the 2 portable generators be in violation of NEC rules about multiple services to a building, (the 2 generators being the multiple services)? Maybe not if there are 2 disconnects grouped together?
Suggestions, comments? Please.
Thanks all,
Rick
A municipal facility has proposed adding 2 5kw portable generators as a backup to the backup automatic generator that picks up the entire building load upon utility failure. The proposal is to install 2 - 30 amp inlets at the same location on the exterior of building. From each inlet we go to a manual transfer switch ajacent to the sub panel served (both sub panels are in the same building but in different locations). These 2 portable generators are not electrically connected in any way. The plan is for these generators to operate at the same time: #1 for the panel that powers the well pump, #2 for the panel that powers vital communications.
Also would there have to be a disconnect for each generator grouped together at the point of entry of both generator feeders? Would the twist lock at each inlet suffice as the required disconnects? The transfer switches are well inside the building.
After thinking on this for several hours a light went on in my head...
Would having the 2 portable generators be in violation of NEC rules about multiple services to a building, (the 2 generators being the multiple services)? Maybe not if there are 2 disconnects grouped together?
Suggestions, comments? Please.
Thanks all,
Rick