gar said:080427-2055 EST
jim dungar:
For a voltage of a given amplitude as you increase the frequency the current thru a capacitor of fixed value will increase, Xc = 1/(2*Pi*f*C). Or for a fixed current amplitude as frequency is increased there is less opposition to current flow. Obviously a function of the load imedance the capacitor sees.
For a given average DC output current from a capacitor input filter the peak input current is much greater than the average ouput current, but short in duration. Maybe 10 times or more. Change to an inductive input filter so that current flows the entire cycle and the input RMS current is quite close to the average DC output current, and thus the peak input current is much lower and of a low frequency than for the capacitor input filter.
Beyond this are currents generated from the switching power supplies driving the motor.
.
Line currents do not cause a GFCI to trip, only leakage current to ground is a concern So if filter capacitors are purposely connected to ground then a GFCI trip is justified..
And yes the frequency of the line currents will affect the coupling capacitance. But this is current on an unintended path and it should be interrupted.