2 ground rods required?

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Back when barns and outbuildings used three arial conductors for feeders (two hots and a neutral) and had a ground rod, was it correct or incorrect to have a N-G bond in the barn's panel?

I'm talking about systems where the service was usually at the house
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Back when barns and outbuildings used three arial conductors for feeders (two hots and a neutral) and had a ground rod, was it correct or incorrect to have a N-G bond in the barn's panel?

I'm talking about systems where the service was usually at the house
there used to be an exception that allowed for this in many cases.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Back when barns and outbuildings used three arial conductors for feeders (two hots and a neutral) and had a ground rod, was it correct or incorrect to have a N-G bond in the barn's panel?

I'm talking about systems where the service was usually at the house
It was allowed.

there used to be an exception that allowed for this in many cases.
The exception still exists for installations that were compliant when they were installed.
 

Electrical Geek

Lead PV Service Electrician
Location
Massachusetts
Occupation
Electrician
Most (not all) jurisdictions around here are fine with one rod and water pipe, or sometimes even two rods if you don't use the water pipe. I think few understand that the code says you still need a 2nd rod even if you have the water pipe. Detached buildings I frequently find done wrong in various ways, I think many inspectors are just not aware of those rules. The biggest AHJs around here enforce things thoroughly.
I find it funny that 250.53(D)(2) states 'A metal underground water pipe shall be supplemented by an additional electrode...'which is singular so we only need one, but then refers us to 250.53(A) for the installation, one would think. If you follow the entirety of that code then you are essentially supplementing the supplemental, which doesn't make sense to me.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I find it funny that 250.53(D)(2) states 'A metal underground water pipe shall be supplemented by an additional electrode...'which is singular so we only need one, but then refers us to 250.53(A) for the installation, one would think. If you follow the entirety of that code then you are essentially supplementing the supplemental, which doesn't make sense to me.
A single rod is not an electrode until it meets the 25 ohms or less test. That's why most guys just install two.
 

Electrical Geek

Lead PV Service Electrician
Location
Massachusetts
Occupation
Electrician
A single rod is not an electrode until it meets the 25 ohms or less test. That's why most guys just install two.
The 25 ohms or less test only applies to whether the supplemental is needed or not, not whether the supplemental needs a supplemental, or am I reading it wrong and why?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
The 25 ohms or less test only applies to whether the supplemental is needed or not, not whether the supplemental needs a supplemental, or am I reading it wrong and why?
250.53(A)(2) requires the rod to have a supplemental electrode of a type specified in 250.52(A)(2) thru (8). That notably excludes 250.52(A)(1), which is the water pipe. So the water pipe cannot supplement the rod.

250.53(D)(1) requires the water pipe to have a supplemental electrode that, if a rod, pipe or plate, complies with entirety of 250.53(A), which in turn requires the additional supplemental electrode that is not the water pipe.

In other words, they very deliberately wrote it to require two rods to supplement the water pipe if you don't have one of the other things like a ufer. Not easy to follow, but very clear once you do.
 

Electrical Geek

Lead PV Service Electrician
Location
Massachusetts
Occupation
Electrician
250.53(A)(2) requires the rod to have a supplemental electrode of a type specified in 250.52(A)(2) thru (8). That notably excludes 250.52(A)(1), which is the water pipe. So the water pipe cannot supplement the rod.

250.53(D)(1) requires the water pipe to have a supplemental electrode that, if a rod, pipe or plate, complies with entirety of 250.53(A), which in turn requires the additional supplemental electrode that is not the water pipe.

In other words, they very deliberately wrote it to require two rods to supplement the water pipe if you don't have one of the other things like a ufer. Not easy to follow, but very clear once you do.
Ok, so, the code requires that, with an underground water pipe, you have to supplement the supplemental. I kind of figured that was how it's being interpreted. Thank you.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
there used to be an exception that allowed for this in many cases.
Yeah, but should the barn fed by 3 wires from the house have a N-G bond? I always felt that it should because it provided a low impedance path in the event of a hot falting to ground. Ground rod alone isn't low enough impedance to blow even a 15 amp fuse
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yeah, but should the barn fed by 3 wires from the house have a N-G bond? I always felt that it should because it provided a low impedance path in the event of a hot falting to ground. Ground rod alone isn't low enough impedance to blow even a 15 amp fuse
Yes, it must be bonded, just like a service, and for the same reasons.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Ok, so, the code requires that, with an underground water pipe, you have to supplement the supplemental. I kind of figured that was how it's being interpreted. Thank you.
You have to supplement the water pipe with another electrode. A single rod can be the other electrode but it requires testing to prove 25Ω or less.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Yeah, but should the barn fed by 3 wires from the house have a N-G bond? I always felt that it should because it provided a low impedance path in the event of a hot falting to ground. Ground rod alone isn't low enough impedance to blow even a 15 amp fuse
Absolutely it needs to be bonded. Lack of bonding at outbuildings, one way or the other, is by far the most dangerous condition that I seem to encounter in the field once a year or so.
 