ASG
Senior Member
- Location
- Work in NYC
- Occupation
- Electrical Engineer, PE
It's still not clear to me what is acceptable in high rise buildings per 700.10(D)
The question is regarding item 1. If you are running horizontally in a hung ceiling or vertically in a shaft, is your cable or raceway in a space or area that is fully protected by an approved automatic fire protection system?
(2) Feeder-Circuit Wiring
Feeder-circuit wiring shall meet one of the following conditions:- The cable or raceway is installed in spaces or areas that are fully protected by an approved automatic fire protection system.
- The cable or raceway is protected by a listed electrical circuit protective system with a minimum 2-hour fire rating.
Informational Note No. 1: See UL 1724, Fire Tests for Electrical Circuit Protection Systems, for one method of defining an electrical circuit protective system. The UL Guide Information for Electrical Circuit Integrity Systems (FHIT) contains information to identify the system and its installation limitations to maintain a minimum 2-hour fire-resistive rating and is available from the certification body. - The cable or raceway is a listed fire-resistive cable system with a minimum 2-hour fire rating.
Informational Note No. 2: See UL 2196-2017, Standard for Fire Test for Circuit Integrity of Fire-Resistive Power, Instrumentation, Control and Data Cables, for one method of defining a fire-resistive cable system. - The cable or raceway is protected by a listed fire-rated assembly that has a minimum fire rating of 2 hours and contains only emergency circuits.
- The cable or raceway is encased in a minimum of 50 mm (2 in.) of concrete.
The question is regarding item 1. If you are running horizontally in a hung ceiling or vertically in a shaft, is your cable or raceway in a space or area that is fully protected by an approved automatic fire protection system?