2" LB Fill Question

Status
Not open for further replies.

Rewire

Senior Member
Ok fellas,

I have only been able to find 2" connectors that will allow me to clamp down on the SER. The supply house could only find 2 ", nothing larger. Therefore, I have to bush down. The inspectors here want the SER clamped as it leaves the conduit. Is there a 2 1/2" connector that I can use on the SER? I simply have to screw it into a female adapter. It does not have to be weather tight.

Thanks,

c2500
threaded reducer 2 1/2 to 2
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Ok fellas,

I have only been able to find 2" connectors that will allow me to clamp down on the SER. The supply house could only find 2 ", nothing larger. Therefore, I have to bush down. The inspectors here want the SER clamped as it leaves the conduit.

334.30 referenced from 338.10(B)4 seems to indicate that it's not required. A strap within 12" of the raceway would suffice.
 