Customer wants to be able to connect a mobile gen to their space. Its a strip mall with 1200 amp 3 ph 208 v service. They use two spaces which means 2 meters for thier store. I would need to feed both panels from this mobile gen.
each meter has a 125 amp molded case breaker next to the meter outside.
I believe this will require 2 auto transfer switches with a common tap box that the mobile gen wires can be landed in. The customer want to supply their already purchased ASCO 300 series 400 amp ATS.
What problem do you guys see with this?
each meter has a 125 amp molded case breaker next to the meter outside.
I believe this will require 2 auto transfer switches with a common tap box that the mobile gen wires can be landed in. The customer want to supply their already purchased ASCO 300 series 400 amp ATS.
What problem do you guys see with this?