2 Meters For 1 Tenant

BatmanisWatching1987

Senior Member
Location
NJ
Occupation
Jr. EE
Designing a strip mall which has a electrical room with 2 separate electrical service of 2 meter bank with 2000 AMP/208V/3P each.

The current space has an existing 200 AMP/208V/3P.
Based on the load calculation, we need to upgrade the service to 400AMP/208V/3P.

One of the existing meter bank of 2000 AMP, has an additional spare which can accommodate an additional 200 AMP/208V/3P breaker.

So can 1 Tenant have 2 separate meter going to the same space.
Does the service have to be from the same meter bank or can it be served for the other bank.

Not sure if I am interpreting the code section 230.2 and 230.3 correctly.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I know of no NEC provision that would prohibit it. The panels would need to be marked to show their supply point.
 

kwired

Electron manager
Location
NE Nebraska
Chances are the utility company will add a 'service fee' to each bill...
And minimum fee for 400 amps very well is higher than for 200 amps, though 2-200's possibly is more than the single 400.

But it possibly can be less when in a multimeter arrangement like this than for stand alone service on stand alone transformer as well.
 
Top