Personally, I don't think that 2 services is compliant or will be allowed.
I would certainly talk to the AHJ before I made any changes.
As iwire posted...The AHJ could allow it per 230.2(C)(3), but if he's like most AHJ's that I "know", I doubt it.
Since there are "two meters and 2 disconnects that are grouped", I assume that the feeders from these "disconnects" to the inside panels are already 4 wire?
If that's the case and you actually need 300A in the building, I would set a 320A meter base and feed these two" main disconnects" from one service, Let the POCO decide how to power it.
That's not a huge job.
If the feeders are only 3 wire, you've got a bigger problem.
steve[/QUOTE
The panels are both 4 wire and i am thinking we will likely be changing this service to one meter and re running wires from meter to transformer.Not cheap at this point but its all on the owner.The meters now are both fed from there own pvc back to transformer 1 1/2 so likely will be running new conduit and wires to supply 300.Will be finding out shortly what the ahj has to say.Prints have yet to be updated and i am sure they will deal with this.