Yep! Measure any one primary to each secondary, in succession of course: H1 to X1, H1 to X2, then H1 to X3. You should get three different voltages, close to the three in the diagram. Same if you measure H2 or H3 to each X in succession, but the voltages won't be in the same order.tommy said:Explain on how I can check as far as lead check Prmary (a) to Secondary (a) then Primary(a) to Secondary (b) and so on for each phases
Check 404.9(B)benaround said:celtic,
250.146(A) , only refers to receptacles, in your 1900 box with Mulbury
cover, if cover is not listed for grounding,then a jumper would be required.
IMO a switch would not. I did mention that adding one would not hurt.
...is misinforming - 404.9(B) indicates when it is required and when it is not.benaround said:When useing metal boxes you do not have to ground to the switch,the 6/32 screws are allowed to ground the yoke. On the other hand, it will do no harm.
I never saw the word "flush" or even "surface" mentioned until now...benaround said:Also, the discussion at the time was talking about 'flush' type boxes and
barriers.
Having multiple sources/supply in a junction box or raceway is not the issue.dcooper said:Tommy I was always taught that you don't have to put a barrier between 120 and 277. just 277 and 277. i did most of my apprenticeship building schools. so there are usually multiple systems in the building.