I'm not sure about new ones. These folks claim to retrofit them:I'm trying like heck to not continue this as I'm sure we all have actual work to do, but:
I've never seen a panel like this with 4 busses plus a neutral....do they even still make them? I guess they need to make it bulletproof so nobody could ever install a 3-phase breaker by accident? All breakers would be 2-pole from this panel (either across A-B or C-D busses)? And all lighting and receptacle panels would be 1-ph, 3-wire loadcenters?
thanks again for all this info....big fan of the site (more of a lurker though).
Here are the connections for 3, 4, and 5 wire:thanks wayne- are you really saying that I can specify as part of my Tenant work a transformer (the Scott T is also new to me.....man I feel like a freshman at college again 20-years ago....just without the mullet) that will essentially turn my service into a 120/240V, 3-phase system where I can supply 120V 1-phase, 240V 1-phase, and 240V, 3-phase loads? I just googled this and it looks like a strange arrangement with a 50% tap on one winding and an 86.6% tap on the other. my overall building load (NEC connected) is 120 KVA.....do they make a 112KVA or 150KVA size for this as a standard?
I have been trying to post a couple JPEG's but have not been successful....any tips on how to do this?
thx
Wayne,Oh but please keep this thread going, I would love to hear the outcome of this one. never ran into a 2 phase feeding a building before, just old draw bridges, and we used a Scott-T to get 3 phase to power the new drive motors when they up graded the drive.
Oh and pleanty of photos is a must![]()
Wayne,
There is a "T" connection and a "Scott" connection. Using the term "Scott -T" can be confusing because they are two different type connections.
??? You should have 170 volts phase-phase if you have 120 volts to the common on a 2-phase.About a year ago, I ran into existing 2-ph power at a site and was getting lost in the coversions and misinformation out there. Fortunately the client changed their mind about what they wanted to do and I was able to put in a new 400A single phase service (only 2phases present on the pole).
I found out that next month the client wants to move into and rehab that building that has the existing 2ph 240 w/ a center tapped phase for 120. Looks like I'll be revisiting this stuff again soon. I'm pretty sure they have 3-phase equipment...![]()
??? You should have 170 volts phase-phase if you have 120 volts to the common on a 2-phase.
Questions:Here are the connections for 3, 4, and 5 wire:
![]()
Those are some engineering symbols used to designate the impedance of the conductors.Questions:
What are the series inductors and resistors in two of the primary conductors?
Yes they can.Can these setups be used in either direction, i.e., 3ph to 2ph or 2ph to 3ph?
Yes.Do these connections allow full use of the transformers' total power ratings?
The series inductors and resistors are for a simple single-phase transformer model consisting of an ideal transformer and a series impedance.Questions:
What are the series inductors and resistors in two of the primary conductors?
Can these setups be used in either direction, i.e., 3ph to 2ph or 2ph to 3ph?
Do these connections allow full use of the transformers' total power ratings?
You can Google: "two phase" powerIs there a book or a web site i can more information on this??
These are variations of a Scott connected transformer (sometimes called a Scott Tee).Is there a book or a web site i can more information on this??