Depending upon how you define your terms and the type of two phase system involved, you may or may not have a root 2 term involved.
If you have a two phase three wire system, with a single common conductor and two phases with 90 degree displacement, and you define voltage as the _phase to phase_ voltage, then power is V * A * sqrt(2) * PF.
If you instead define the V used in your equation as the _phase to common_ voltage, then the answer is V * A * 2 * PF.
You see the same duality in the common three phase calculation. When V is the line to line voltage, and all phases carry the same current, then power delivered is V(LtoL) * A * root(3) * PF. If you instead quoted the line to neutral voltage, then the power delivered is V(LtoN) * A * 3 * PF. The latter equation is much less commonly used, but it is the equivalent of the first equation. Remember that for a three phase wye system, V(LtoL) = root(3) * V(LtoN)
For a six phase system, you need to similarly define what voltage you are looking at, L-N or L-L. Additionally, there are two common six phase systems, one with 60 degree phase displacement (which for motors is the equivalent of common three phase with 120 degree displacement), the other with two 120 degree three phase sets, 30 degrees apart. The latter system has uneven phase displacement, and thus a poorly defined V(LtoL).
-Jon