Hi Guys , Need to throw this out there, never had to do this permanently and dont feel comfortable that its even gonna work. Here goes ....
Need to electronically meter a 20a, 2 pole circuit breaker to an electric heat load thru the use of CT's. The unit and display for the CT's will need 120volts. Is it NEC compliant to tap into this 20amp, 2 pole breaker that has a handle ty with #12 thhn to obtain 120volts ?
Thanks, Mike
(now that I think of it the 2 pole CB with a handle ty would still protect the thhn, it would be like having a multi-wire circuit [12-3] , and using a handle ty.)