2-pole, 3-wire, grounding type receptacle?

Status
Not open for further replies.

rrc14

Member
Location
Anchorage, AK
Occupation
Engineer
What is the difference between a 2-pole, 3-wire, grounding type receptacle and a regular 2-pole, 3-wire receptacle? Does the regular 2-pole, 3-wire receptacle not have ground?

Thanks for any information.
 
rrc14 said:
What is the difference between a 2-pole, 3-wire, grounding type receptacle and a regular 2-pole, 3-wire receptacle? Does the regular 2-pole, 3-wire receptacle not have ground?

Thanks for any information.

Here ya go:
nema-config-1ph-250v.gif
 
rrc14 said:
What is the difference between a 2-pole, 3-wire, grounding type receptacle and a regular 2-pole, 3-wire receptacle? Does the regular 2-pole, 3-wire receptacle not have ground?

Thanks for any information.

I wonder if they are not the same. Where do you see this wording of the devices.
 
Okay, I was just thrown off by the phrase "grounding type", I see know all that means is a receptacle with a ground. The "regular" receptacle I was alluding to was a "grounding type" all along. thanks guys for the clarification.

RC
 
Status
Not open for further replies.
Top