2 Pole GFCI Breaker Load Neutral Requirement

cpminn

New User
Location
Morristown, NJ
Occupation
Project Director
Does a Siemens QPF 2 pole GFCI Breaker require a load neutral to operate properly and meet 2020 NEC Code Requirements? This breaker is feeding a NEMA 14 50 R Receptacle for a Electric Vehicle.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Only if the receptacle has a neutral connection, which the 14-50r does, even though most new chargers do not use it. Older chargers used the neutral for control power for the controller. The neutral is not used by the EV.
 

kwired

Electron manager
Location
NE Nebraska
No load side neutral is required for the GFCI breaker to function.

Could even have a 120 volt circuit connected to it and not use one pole and it still would function.

If it has line side neutral connection it must be connected or the GFCI logic will not function. Plus you would have open neutral condition if there were a load side neutral conductor utilized.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Plus you would have open neutral condition if there were a load side neutral conductor utilized.
That would apply if you leave the load side neutral connected. It would not apply if instead you connected the load side neutral to the neutral bar instead of a neutral pigtail on the GFCI breaker, but the GFCI still might not work properly.
 