2 pole gfci breaker

Status
Not open for further replies.

bluecollar84

Senior Member
Location
US
Hi I have a 2 pole 15 amp gfci breaker that I'm using for my AC condensor Will this work for stright 240v loads with no load neutral attached to the gfci ? The condenser doesn't require a neutral it's straight 240v but the manual that came with the condenser said it wants a gfci protected circuit. The breaker I bought is a Murray mp215gf

Sent from my SM-G935V using Tapatalk
 
Hi I have a 2 pole 15 amp gfci breaker that I'm using for my AC condensor Will this work for stright 240v loads with no load neutral attached to the gfci ? The condenser doesn't require a neutral it's straight 240v but the manual that came with the condenser said it wants a gfci protected circuit. The breaker I bought is a Murray mp215gf

Sent from my SM-G935V using Tapatalk

You don't need the neutral to use that GFCI.
Never saw a condenser requiring such a breaker.
 
f6c2fcf67f78f1e55edeea4155fc882b.jpg


Sent from my SM-G935V using Tapatalk
 
"Depending on the installation area..."
That makes this just a CYA statement on their part. Puts the onus on you to decide if it needs it.
I agree.

Risk involved with "hardwired" equipment is usually minimal compared to cord and plug connected equipment, and I still feel there have been some GFCI requirements added in recent years that are not all that necessary.
 