I have never heard of someone, defeating a GFCI breaker simply by removing the line side neutral, have you? If it worked how many people would do it to prevent 'nuisance trips'?
First, that concept would only work for straight 240 volt loads, any 120 volt loads in the circuit and it is tripping anytime the 120 volt load turns on.
I don't know all the technicalities of the control portion of these devices.
A few questions I don't have the answer's to:
Do they need both ungrounded and the grounded conductor before they will reset (2 pole units)?
If the grounded conductor is part of the "control" circuit, why should we epect it to trip with part of control circuit missing?
If grounded conductor is required for it to operate properly, why aren't they more like GFCI's for portable cordsets, requiring full power to be present before it will reset, and it would also trip anytime power is lost?
If they do trip upon loss of the grounded conductor, why not (or maybe they do) trip upon loss of an incoming ungrounded conductor? Especially if that conductor is a part of the control circuit.
I know GFCI receptacles are currently designed that they must have proper line/load polarity to reset, but once they are reset, you can cycle power on/off all you want, or even open either the grounded or ungrounded conductor and it will not trip. I don't know if it would trip upon imbalanced current should that condition exist even though one supply conductor may be open. If it does, where is control power to operate the trip coil coming from?