iwire said:
jim dungar said:
iwire said:
I will say I am confused.
IF I install a 3 pole breaker in a single phase panel and only use the outer poles I will be using the same phase for each conductor.
I have no idea why I would want to do that.
You are reading slightly out of context. The original statement was an example of how a 3-pole breaker
might be labeled.
I see now, thanks. :smile:
I'm glad you understand. . I wish I did also. . But I don't. . Altho I didn't specifically state it, that was part of my original problem with that whitebook paragraph. . I couldn't make sense of all of it and still can't.
The 2
differences between the 2 sentences seem to be obvious enough.
dnem said:
UL Molded Case Circuit Breakers Marking Guide '07
page 17
33. 3-Pole - 1-Phase Rated - 3-pole circuit breakers are suitable for use on 3-phase systems only, unless marked to indicate use on 1-phase systems, such as, "For 1-phase connections, use two outside poles," or an equivalent statement. A 3-phase breaker used in place of a 2-pole breaker on a 3-phase system, such as a 2-pole breaker used in a branch circuit that is actually two legs of a 3-phase system, is acceptable without the 3-pole breaker being specifically marked.
Sentence 1 - single phase system/panel
It starts out talking about 3 phase,
"3-pole circuit breakers are suitable for use on
3-phase systems only, ....."
and then switches to give direction for single phase,
"..... unless marked to indicate use on
1-phase systems, such as, "For 1-phase connections, use two outside poles," or an equivalent statement."
single phase - "marked to indicate use"
Sentence 2 - 3 phase system/panel
This sentence flips back to 3 phase,
"A 3-phase breaker used in place of a 2-pole breaker on a
3-phase system, such as a 2-pole breaker used in a branch circuit that is actually two legs of a 3-phase system, is acceptable without the 3-pole breaker being specifically marked."
3 phase - "without ..... being specifically marked"
Going back to the single phase system/panel, can anybody give me even one single example of when you could terminate on a 3pole breaker "For 1-phase connections, use two outside poles" and get anything other than 2 of the
same hots ? . Is there
any situation/configuration where you could land 2 wires on the outside poles of a 3pole breaker in a single phase panel and energize the load ?
jim dungar said:
The original statement was an example of how a 3-pole breaker might be labeled.
Can you give me one example of when the 3 pole breaker might be labeled, "For 1-phase connections, use two outside poles", an example that stays within the context of the sentence that is giving direction about use in a single phase system/panel ?
David