2 poles shared Neutral

Status
Not open for further replies.

cadpoint

Senior Member
Location
Durham, NC
Occupation
Electrician - but not by NC Law.
I never gave it a thought but I can across a shared neutral on both poles of 120/240.
I had to take a double look on that. It general branch receptacles service, residential.
Anything up with that? Should I throw a penalty flag ...
 
cadpoint said:
I never gave it a thought but I can across a shared neutral on both poles of 120/240.
I had to take a double look on that. It general branch receptacles service, residential.
Anything up with that? Should I throw a penalty flag ...
MWBC ..multi wire branch circuit
From 100:
Branch Circuit, Multiwire.
A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
Eyeball 210.4

Here's the commentary following 210.4 from the NECH:
Multiwire branch circuits can be dangerous. Section 210.4(B) specifically requires simultaneous disconnection of all ungrounded conductors and requires that it take place at the panelboard of origin. The reason for this requirement is to reduce the risk of shock should a worker fail to disconnect all of the ungrounded circuits to the equipment mounted on a single yoke or strap of a device. Most commonly, receptacles are the focus of this requirement. However, equipment mounted on a yoke can include devices such as receptacles, switches, and lampholders, as well as other items such as dimmers, pilot lights, and home automation controls.
Many 125-volt, 15- and 20-ampere duplex receptacles have a break-off tab that permits each of the two receptacles to be supplied from different circuits or a 3-wire (multiwire) branch circuit. This arrangement is commonly called a split-wired receptacle (i.e., one circuit supplies half the duplex receptacle and another circuit supplies the other half). The simultaneous opening of both ?hot? conductors at the panelboard effectively protects personnel from inadvertent contact during servicing with an energized conductor or device terminal. The simultaneous disconnection can be achieved by a 2-pole circuit breaker or by two single-pole circuit breakers with an approved handle tie, as shown in Exhibit 210.1 (bottom). If fuses are used, a 2-pole disconnect switch is required.
 
Thanks Celtic. Flare's UP ! 210.4(C) & didn't even make the Exceptions... :rolleyes: Most be slow in da Heat, Be Safe !
 
This shared neutral that you've mentioned is no different than the shared neutral feeding the service in the residential panel.
 