2 romex cables 12/2, why they do this?

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
I don't have code articles handy, but I have checked before and because it is acceptable do this kind of thing quite often.

Even is acceptable with metal box/enclosure if using a connector rated to handle both cables involved.

Uses more copper than say 12-2-2 (which has one less EGC) but they seem to be proud of the price with 12-2-2.
Bathroom fan/light/heater - I almost always run power to switch box than 2 - 12-2's to the unit.
 
Interesting responses.

This scenario I have seen here is the main feed hot and neutral was ran to the light box first then the (hot only) to the switch box. So basically if they have the hot and neutral in one cable and the switch legs in the other cable, the switch leg cable wont have the counter emf to reduce the inductance/heat. I thought this was a code violation . If they use both cables as just a hot and switch legs , one for fan and one for light, then there is no neutral at the both, which is also a code violation.

Am I still missing something here?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Interesting responses.

This scenario I have seen here is the main feed hot and neutral was ran to the light box first then the (hot only) to the switch box. So basically if they have the hot and neutral in one cable and the switch legs in the other cable, the switch leg cable wont have the counter emf to reduce the inductance/heat. I thought this was a code violation . If they use both cables as just a hot and switch legs , one for fan and one for light, then there is no neutral at the both, which is also a code violation.

Am I still missing something here?
Yes. For balanced current to flow in a pair of conductors, it is not necessary for one of them to be a neutral (grounded). A hot to a switch and the return to the light will also carry the identical current.

Having a neutral to a switch has nothing to do with the above comment; it's for electronic switching.
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
I'm going with the person who speculated that they didn't have 12/3 on the truck. There is just no other reason to do this.
 
Yes. For balanced current to flow in a pair of conductors, it is not necessary for one of them to be a neutral (grounded). A hot to a switch and the return to the light will also carry the identical current.

Having a neutral to a switch has nothing to do with the above comment; it's for electronic switching.
I understand that about the balance current flow, i was looking at how they they may have this going without it technically being a code violation. I still see a code violation on a technicality. Like i said, if they use each cable as a hot and switch leg for the 2 switches they will have balance current flow, but then the there is a code violation because there is no neutral at the 2 switch box per the new requirements of the nec because the source feed is at the ceiling fan light box.

If they use one cable as a hot and neutral (just to get the neutral at the box per nec) then the other cable will have the 2 switchlegs but then its a code violation because the 2 switchlegs cable will not have the counter emf to cancel out. That neutral requirement for switches at their location (just the possibility of future automatic switches) makes things a little more challenging .

and yes I do believe that 12/2 cable is probably all they had on the truck at the time, but its still a code violation from the way the install is done.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Like i said, if they use each cable as a hot and switch leg for the 2 switches they will have balance current flow, but then the there is a code violation because there is no neutral at the 2 switch box per the new requirements of the nec because the source feed is at the ceiling fan light box.
The simple solution is to use one re-colored white to feed both switches, and the other white for the neutral.
If they use one cable as a hot and neutral (just to get the neutral at the box per nec) then the other cable will have the 2 switchlegs but then its a code violation because the 2 switchlegs cable will not have the counter emf to cancel out.
As long as the two cables are run together, especially through KOs in metal, there is no induction problem.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
The key to the fields around the wires balancing is their proximity and the materials between them.

Take the situation you are concerned about. It would be a code violation to run the conductors in separate emt raceways.

It would be a code violation to run the conductors in separate MC cables.

In fact in general what you describe is a code violation.

But in the specific case of NM cables and NM boxes, or NM cables all passing through the same openings in metal boxes, the inductive effects are small enough that code permits the installation.

Additionally if the two cables are run side by side the magnetic cancellation is effectively the same as a single cable enclosing all the conductors.

You are exactly right about the voltage and current balancing effects. It is simply that for NM cables the effects are small enough that code permits the installation.

Jon
 

kwired

Electron manager
Location
NE Nebraska
Or a 12-2 and a 12-3 for a fan/light/heater/night-light combo.
done that as well.

Also have run two 2 wire cables between switch boxes when needing both L1/L2 as well as a set of three way traveler conductors between those two boxes. Using a 3 wire cable as one of them uses 1 more conductor than you actually need.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Also have run two 2 wire cables between switch boxes when needing both L1/L2 as well as a set of three way traveler conductors between those two boxes. Using a 3 wire cable as one of them uses 1 more conductor than you actually need.
Especially when done a lot, like I described here:
 