Here is a debate I’ve had with a few people. Large building has one service owner decides to partition off a section and rent that part. Original service is 1200 amps with water main grounding electrode sized at 3/0, CEE #4 sole connection, building steel 3/0, 2 ground rods with # 6 sole connection all tied together at main service neutral bus. The new section of the building gets special approval for a second service 400 amps. Here is were the debate begins on the new service one argument is that service needs all electrodes described above and sized based on the new service conductor size and the other argument is it would only need to go to building steel based on the new service conductor size.
The two services are 400' apart and all the original electrodes are by the first service.
2005 NEC
I would like to hear your thoughts on this subject.
Code sections would be nice.
I know what side of the debate I’m on just would like some more opinions
Hope I've given enough info. Any question I'll try to answer
The two services are 400' apart and all the original electrodes are by the first service.
2005 NEC
I would like to hear your thoughts on this subject.
Code sections would be nice.
I know what side of the debate I’m on just would like some more opinions
Hope I've given enough info. Any question I'll try to answer